HVAC cooling & heating load calculations on the PE Mechanical exam

Load calculations sit at the center of the HVAC & Refrigeration depth — they feed equipment sizing, airflow, and psychrometrics, so the math here shows up everywhere. The good news: most of it reduces to a handful of standard-air relations you can apply fast once they're automatic.

What you actually need to own

  • The standard-air shortcut relations (sea-level, standard air):
    • Sensible: Q_s = 1.08 × cfm × ΔT (Btu/h), with ΔT in °F.
    • Latent: Q_L = 0.68 × cfm × ΔW (Btu/h), with ΔW in grains of moisture per lb of dry air.
    • Total: Q_t = 4.5 × cfm × Δh (Btu/h), with Δh the enthalpy change (Btu/lb).
    • Know that these factors come from standard-air density and must be corrected for elevation or low temperature when the air isn't standard.
  • The cooling-load components: conduction through the envelope (U·A·ΔT, or a cooling-load temperature difference method), solar gain through glazing, internal gains (people — sensible + latent, lights, equipment), and infiltration/ventilation (both sensible and latent).
  • The heating-load components: conduction losses (U·A·ΔT) and infiltration/ventilation — typically without crediting solar or internal gains (the conservative design condition).
  • Sensible heat ratio SHR = Q_s / Q_t, which ties the load back to the psychrometric coil process.

Where people lose points

  • Mixing up the factors — using 1.08 (sensible) on a latent or total quantity, or vice versa.
  • Forgetting elevation/temperature corrections to the standard-air factors — the exam specifically tests non-sea-level air.
  • Dropping the latent side of people and ventilation loads, or the latent portion of infiltration.
  • Confusing heating and cooling assumptions — crediting solar/internal gains on a heating load.

How to study it

Drill the three air-side relations until the factor and units are reflexive, then practice full component-by-component load problems — envelope + solar + internal + ventilation — so you don't miss a term under time pressure. Tie every result back to the psychrometric process so the load and the coil are one picture, not two.

Part of the HVAC & Refrigeration exam. → Start your 7-day free trial — no card.

Put it into practice.

Exam-real problems with a grounded AI tutor on every one — Handbook-cited solutions, full mock exams, and a diagnostic — for the exam you’re sitting, on the current spec. Available today for the PE Mechanical exams, with PE Electrical: Power in build now. Seven days free, no card.